80 charger requires a 100 amp feed using #3 CU wire as per the NEC; the extra outlet shall be on its own separate circuit! Also you want the contractor to pull a permit, the link below will guide you to some of the best EC's around San Diego.Thanks for the input.
I’m thinking Lucid 80 amp charger + hardwired & extra outlet at the moment.

NECA San Diego | Advocacy, Education and Business Development
NECA San Diego supports its members by providing Political Advocacy, Labor Relations, Education, Business Development, and Much More! NECA San Diego represents more than one hundred electrical contractors who bring power, light, and communication technology in San Diego and Imperial Counties.

NEC Section 625.41 requires the OCPD for a branch-circuit or feeder(s) supplying EVSE to be sized at 125% for continuous loads.