The sizes below are based on the NEC and will work for the majority of installations, but consult a licensed electrician to confirm.
Breaker and wire size table, for copper only:
View attachment 7710
Based on 122ºF ambient temps per NEC 310. For single-circuit raceways only.
Runs longer than about 100 ft, wires run through an attic, and multiple circuits sharing the same conduit may require larger wire sizes.
Breaker sizes larger than 50A must be hardwired directly to the EVSE.
A neutral wire is not required unless feeding a NEMA 14-50 receptacle, then it must be included.
The 100A circuit is included for maximum power from the LCHCS.
* One update on the charging speed; I pulled this chart from an F150 Lightning forum where the onboard charger is limited to 48A.
For a 70A breaker, you can charge at up to 50A on some of the hardwired chargers.
With the LCHCS, you’ll be able to use the full “Max load” all the way up to 80A on a 100A breaker, provided you have the right sized wiring, breakers, panel, and everything else.
Please consult an electrician unless you are doing a “like for like” exchange, and even then I’d recommend it.