If I install 3AWG or 2AWG wire and 1/4" compression lugs with a 50-amp circuit breaker, what should my charging rate be using the Lucid charger?
 
Charging current is always limited by the circuit breaker, assuming the wires and chargers are rated for the current. In your case, I guess it's the breaker so (50x0.8) x 240V = 9.6kw
If your panel allows, you may be able to go for a higher amp circuit, if you are using Lucid home charger. For the mobile charger that came with the car, 9.6kw is the limit
 
If I install 3AWG or 2AWG wire and 1/4" compression lugs with a 50-amp circuit breaker, what should my charging rate be using the Lucid charger?
If your concern is reducing the cross-section area using the compression lugs, then the generic answer would be to introduce as fewer amps through that cross section as are acceptable to you to hit a certain charging rate that works for you if charging overnight. For similar reasons, I keep my charging rate to 30 amps because it doesn't let the battery cooling fans turn on. I could do the math but don't feel like busting on the laptop to pull up my conduit and cable NEC calcs spreadsheet I've been using for 20 years. 😀
 
80% of the 50 amp or 40 amp. The larger wiring is a waste, unless you ever plan to upgrade your panel and add a larger breaker for the charger.
 